  1. M

    Electric heaters and extension cords

    the heater is a continuous load, so whatever is powering it needs an ampacity of 15.625 amps (20% derating)
  2. M

    Florescent bulb flashes in a parallel circuit?

    might be a 'bootleg' 3 way, where the line to the lamp is switched between hot an neutral
  3. M

    #4 or #6 for the shop?

    you guys are missing the 'Type TC' thats tray cable which is a NEC cable type, usually suitable for direct burial and sunlight exposure. I dont know if and where its allowed in residential uses. The STO is a dual listing. (I would love to see a product listed as STOW/TC-ER/NM-B/UF-B)
  4. M

    #4 or #6 for the shop?

    does it have 3 or 4 wires in it? does it say its listed for direct burial? the STO would make it a cord which you couldnt use but it appears to be dual listed as tray cable which you *might* be able to use. The best move would be to sell it as its worth alot more than the proper cable for your...
  5. M

    BIG spark when plugging stuff in! - possible CFL issue

    CFLs are basically a dead short for one cycle when first energized.
  6. M

    Dream lighting ! cost no object

    if cost were no object i would buy a lifetime supply of every version of incandscent and halogen lamp I think I could ever use, and set up a fund to pay for the electricity and air conditioning.
  7. M

    Wiring Two 1500W circuits, help needed....

    are you supposed to use GFCI with those or GFEP which has 30ma trip?
  8. M

    low wattage flood (PAR38) bulbs?

    you can get par 30 and par 20 in lower wattages -35w i think. Also get a 130v lamp as it will be a bit dimmer (and last longer)
  9. M

    Can you combine low voltage (thermostat) and line voltage in a conduit?

    isnt a thermostat class 2? in which case it cant occupy the same raceway with class 1 circuit
  10. M

    Light/Vent over shower

    fantech = the best bathroom fans ever. No big ugly square, super quiet, and they have one with a light in the center of the air intake http://residential.fantech.net/residential-products/bath/single-grille/ click the tab for lighted intakes
  11. M

    Subpanel boding/unbonding

    Did your handyman install SE cable underground in conduit? I though SE couldnt go underground as its not ok for wet location....
  12. M

    Subpanel boding/unbonding

    and WHATEVER you do dont keep the existing feeder, isolate the neutral and ground, add a ground rod and think youre ok. People have been killed from this sort of thing.
  13. M

    Backup generator with solar PV setup

    does the inverter have an islanding mode? maybe add some batteries and omit the generator
  14. M

    Backup generator with solar PV setup

    my answer would be maybe. depends on how sensitive to grid frequency the inverter is, and the quality of the generator. I have a feeling it would work when you first fire it up, but then every time a load is switched on and off the inverter would trip offline.
  15. M

    Overhead Receptacle... How to keep plugs from falling out

    Hospital grade receptacles have the most holding force. Use one and your plugs will not fall out.
  16. M

    Q on installing 2-2-2-4 Al SER in conduit

    Yes, 53% fill so youre ok wiht 1-1/4" conduit. Conduit bodies however have restriction on conductor size due to bend radius. Here is a handy chart http://www.cooperindustries.com/content/dam/public/crousehinds/Industrial%20EX%20Products/Other%20PDFs/Industrial%20Fittings%20Wire%20fill%20chart.pdf
  17. M

    Q on installing 2-2-2-4 Al SER in conduit

    Biggest conductor allowed in a regular 1-1/4" conduit body is #2, and 2-2-2-4 SER comes out to 900 and something MCM. (unless im looking at this wrong). Why not use individual conductors in the conduit?
  18. M

    Q on installing 2-2-2-4 Al SER in conduit

    I think you are way over the fill limit putting 2-2-2-4 AL SER in 1-1/4" conduit, not to mention the fill and bend radius in the LB. Is the entire run in conduit? If so use individual conductors, not SER.
  19. M

    How many 220v outlets?

    as far as multiple outlets on one circuit, it doesnt have anything to do with voltage it has to do with connected load. Basically the rule is this: If the equipment being powered is fixed in place, and it draws 50% or more of the circuit ampacity it has to be on its own circuit (and 'i wont run...
  20. M

    interlock generator switch 2 main panels

    they do. both SQD and CH have similar things.